Had this exact issue last year with my emergency backup setup. The MultiPlus is brilliant kit but it absolutely hates high inrush loads — well pumps are notorious for it because a typical submersible can pull 6-8x its running current on startup.
A few things worth checking:
Transfer switch timing — if you're running the MultiPlus in UPS mode, tighten up the transfer time. Sometimes the pump catches the inverter mid-transition and the sudden load spike triggers the overload protection.
PowerAssist settings — if you've got mains input available, make sure PowerAssist is actually enabled in VictronConnect. It should help buffer those startup spikes by drawing from both battery and grid simultaneously.
Soft starter — honestly the most reliable fix I found was fitting an external soft starter on the pump motor itself. A Sollatek or similar unit costs £40-80 and reduces that inrush dramatically. Made a night-and-day difference on mine.
Battery cable sizing and connections — loose or undersized cables cause voltage sag under inrush, which the MultiPlus interprets as a fault condition. Worth double-checking your connections are properly torqued.
What MultiPlus model are you running and what's the pump rated at? The 1600VA units will struggle more than the 3000VA with anything above a 750W pump motor. Also worth checking the #overload fault log in VEConfigure — it'll tell you whether it's tripping on current or voltage limits.
Anyone else tackled pump loads with their Victron setup? Curious whether the newer MultiPlus-II firmware handles inrush any better than the older units.