Had the exact same issue when I first tried running a compressor off my Multiplus-II 3000. Induction motors are brutal on startup — the inrush can be 6-8x the running current, which catches the inverter completely off guard even if the running load looks fine on paper.
Few things worth trying:
- Check your assistant settings in VictronConnect — specifically the overload trip delay. You can sometimes tweak this to give it a bit more headroom before it throws in the towel
- PowerAssist — if you've got any grid or shore power available as backup, enabling this can help bridge that startup spike
- Soft starter — genuinely the easiest fix. Picked up a cheap one for around £40 and it transformed things. Fitted it inline with the motor and the startup draw dropped massively
Also worth knowing what your battery setup is. If you're on lithium (I run Fogstar cells) the BMS can sometimes be the culprit rather than the Multiplus itself — a sharp inrush triggers overcurrent protection on the battery end and the whole thing collapses before the inverter even reacts properly.
What size Multiplus have you got and what's the lathe motor rated at? A 5.5kW motor on a 3kVA inverter is just never going to work without a soft starter regardless of settings.
Others on here have had good results with the Victron ESS assistant tweaks too — worth a search through the old threads.
What's your current battery bank and cable setup like? Undersized cables can make this significantly worse.