Had this exact issue last year with my Multiplus 2 (3kVA). Microwave was constantly tripping it out — turned out to be a combination of the surge and the PowerAssist settings not being configured properly.
Few things worth checking:
- What's your
AcInputCurrentLimitset to? If it's too low, the Multiplus can't blend grid/shore power fast enough when the surge hits - Dynamic current limiter — worth enabling in VEConfig if you haven't already. It gives the inverter a bit more headroom to ramp up without tripping
- Battery state — if your bank is low or your BMS is throttling output, the inverter won't have the grunt to absorb that initial spike
Microwaves are notoriously spiky — the magnetron startup can pull 2–3x the running wattage for a fraction of a second. My old 800W microwave was pulling nearly 2.2kW on startup according to the Cerbo logs.
Also worth checking which transfer switch speed you're on. Fogstar Drift cells can handle high discharge bursts fine, but if your system is grid-tied and the transfer isn't fast enough, you get a brief undervoltage that causes the trip rather than the surge itself.
What inverter firmware are you on? There were some known issues in older versions with overload sensitivity being a bit hair-trigger.
Anyone else had this on a purely off-grid setup (no grid input at all)? Curious whether it behaves differently without the PowerAssist logic in the mix.