Had this exact issue last summer with my shepherd's hut setup. The Multiplus 12/3000 would trip the moment the washing machine's heating element kicked in — classic inrush current problem rather than a sustained overload.
Few things worth checking:
1. PowerAssist settings
If you're running shore power or a generator alongside, make sure PowerAssist is actually enabled in VictronConnect. It lets the inverter draw from both sources simultaneously to cover those spike loads.
2. Dynamic Current Limiter
Enable this in the settings. It tells the Multiplus to be more forgiving about brief current spikes rather than tripping immediately.
3. Battery state and cable gauge
A battery that's below ~50% SOC will sag under load, which the inverter interprets as an overload condition. Also worth checking your DC cable runs — voltage drop on undersized cable can trigger the same behaviour. I was running 35mm² initially and upgraded to 70mm² which made a noticeable difference.
4. Which Multiplus exactly?
The 12/3000 is borderline for a washing machine with a full heating element — some machines pull 2,200W sustained during the heat cycle. The 24V or 48V versions handle this more gracefully. Worth looking at your machine's actual rated wattage rather than the drum capacity.
What battery chemistry are you running? LiFePO4 will handle the discharge spikes far better than AGM. My Fogstar Drift cells barely flinch at 150A draw whereas my old Trojan AGMs used to sag badly.
What does your VRM portal or the Multiplus LEDs show when it trips — is it the overload indicator or the low battery warning lighting up?