Had almost the exact same grief last winter on the narrowboat. The spin cycle on our little Bosch draws a massive surge the moment it kicks in — the Multiplus II 3kVA was seeing it as an overload and shutting down before it could even react properly.
Few things that sorted it for me:
- Check your
PowerAssistsettings — if shore power or a generator is in the mix, make sure it's configured to pull from both sources during peaks rather than relying solely on the inverter - ESS assistant vs standalone — I had the wrong assistant loaded which was making the overload threshold behave oddly
- AC output cable sizing — undersized cable creates voltage drop which the Multiplus reads as a heavier load than it actually is
The fix that actually cracked it was bumping the overload trip delay slightly in VE.Configure. By default it's quite aggressive, and a washing machine's spin surge is brief enough that a tiny bit of tolerance makes all the difference without compromising protection.
Worth also checking whether your battery can actually deliver the surge. I'm running Fogstar Drift 200Ah LiFePO4 and even that had some BMS hiccups early on when the surge hit — the BMS was cutting out a split second before the Multiplus could compensate.
What battery setup are you running? And is this a 2kVA or 3kVA unit? Makes a difference to what headroom you've actually got.
Others on here will have thoughts — @anyone running larger Multiplus setups, curious whether the 5kVA handles spin cycles without any tweaking or whether it's still a faff.