Had the exact same issue on my narrowboat last summer — Multiplus II 3000VA kept throwing a low voltage alarm and shutting down the moment the spin cycle hit. Turned out to be a combination of factors rather than one single culprit.
A few things worth checking:
- Battery cable sizing — even a short run of undersized cable creates enough voltage drop under surge load to trip the unit. I went up to 70mm² and it made a noticeable difference
- DC fuse/breaker rating — some cheaper ANL fuses are slow to respond and can cause odd behaviour under surge
- Transfer switch settings in VEConfigure — there's a
dynamic current limiteroption that's worth enabling if you haven't already
Also, what's your battery setup? I'm running Fogstar Drift LiFePO4 and found the BMS was momentarily disconnecting under high surge draw, which looked to the Multiplus like a dead short. Completely separate problem from the inverter itself but produced identical symptoms.
The washing machine motor surge on spin is brutal — can be 3-4x running current for a second or two. If your Multiplus is already working hard (say you've got a garden office or EV charger pulling load simultaneously), it doesn't take much to push it over the edge.
What VA size is your unit and how many cells/what capacity are you running on the battery side? Might help narrow it down.