Had this exact problem last summer in the cabin. Multiplus 2000VA kept dropping out the moment the spin cycle kicked in — that inrush current from the motor is brutal, even on a modest machine.
A few things worth checking:
- Transfer switch sensitivity — the Multiplus can be twitchy about what it considers an overload. Dig into VE.Configure and look at your AC Input Current Limit and the overload trip settings. Mine was set far too conservatively from the factory.
- Battery voltage under load — if your bank sags below the low voltage cutoff during that spike, it'll trip on voltage rather than current. I was blaming the inverter for months before I realised a weak cell was dragging the whole bank down under heavy draw.
- PowerAssist — if you're running shore power or a generator alongside, make sure PowerAssist is actually enabled and configured properly. It exists precisely for these surge moments.
My fix ended up being a combination of adjusting the overload trip delay in VE.Configure and replacing a tired AGM with a proper Fogstar Drift lithium cell. Night and day difference once the battery could actually deliver the amps without wobbling.
What inverter size are you running, and what's your battery setup? A 2000VA is genuinely marginal for a washing machine — some spin motors pull 2000W+ at peak inrush, which gives you essentially zero headroom.
Others had similar grief here before — worth hearing whether this is a settings issue or a capacity issue for your particular setup.