Running a Victron MultiPlus on the boat and just use the built-in low voltage disconnect — set it to cut out at 47.5V (12V bank so roughly 11.9V equivalent scaled up... wait, I'm on 48V 😅) and it's been rock solid honestly.
For the startup side I've got a Cerbo GX doing the heavy lifting. Set up a simple automation in VRM so the inverter won't come back on until the bank recovers to 52V or so — stops it from cycling on and off when the sun's barely tickling the panels.
Before I had the Cerbo I was using a cheap relay module triggered by a Victron Battery Sense, which worked surprisingly well for the price. Bit janky but got the job done over one winter.
Few things I'd suggest regardless of setup:
- Always add a time delay before restart, not just voltage — avoids false triggers from brief regen spikes
- Log your cutoff events if you can, tells you a lot about your usage patterns
- Don't rely solely on inverter-level protection, a proper BMS should be your last line of defence (Fogstar Drift cells have decent built-in protection on that front)
Curious what others are doing — especially anyone running a more DIY route without the Victron ecosystem. Seen a few posts about using ESPHome or similar for this and wondering if anyone's actually running that day-to-day on a liveaboard situation where reliability actually matters.