Finally got round to sorting proper hot water in my garden office and I'm debating the cable sizing. The office is about 14 metres from the house consumer unit, and I want to run a dedicated circuit for a 3kW immersion heater (standard 13A draw). I've already got a 32A MCB spare in the CU and was thinking 6mm² T&E for the run, mostly clipped direct under the floorboards and through the cavity. Some people are saying 4mm² is fine for 13A but I always feel happier going a size up, especially with the length of the run.
The main reason I'm leaning toward 6mm² is the voltage drop. By my rough calculations on a 14m run at 13A, even 4mm² should technically come in under the 3% threshold, but it's tight. 6mm² gives a fair bit more headroom and the cable cost difference is maybe £25 for the whole roll, which feels like a no-brainer to me.
Anyone else run a dedicated immersion circuit to a garden office or outbuilding? Curious whether you went T&E or SWA for the outside section — I've got about 4 metres that'll need to go underground across the garden path. Was planning to sleeve the SWA in conduit for that bit but not sure if that's doubling up unnecessarily.