Bit of a rabbit hole this one, but bear with me — had something similar crop up with my Multiplus II last winter that had me questioning my own sanity (and my 20-odd years of marine electrics experience, which is frankly worse).
The short version: my AC loads were reading noticeably higher in VRM than what I could account for by physically measuring each circuit with a clamp meter. Talking a solid 15-20% discrepancy, not just rounding noise.
Turns out the MP II's internal consumption — transformer losses, idle draw, the whole lot — was being lumped into the "AC Loads" figure rather than shown separately. Victron's own documentation is, shall we say, interpretively flexible on this point.
A few things worth checking if you're seeing similar:
- ESS assistant vs. no assistant — changes how loads are calculated and displayed in VRM entirely
- Grid metering vs. inverter metering — are you using an external EM24 or relying on the internal figures?
- Multiplus input current limit — if it's throttling AC in, the maths gets creative
Running a Fogstar Drift 48V LiFePO4 bank here, so I'm particularly twitchy about accurate load readings feeding into my SOC calculations — garbage in, garbage out as they say.
Curious whether anyone else has cross-referenced their VRM AC loads against a proper sub-meter on the distribution board? I'd love to know if this is purely a display/calculation quirk or something worth raising with Victron support directly.