Bit of a tangent from the solar controllers subforum but feels relevant enough — has anyone successfully got a conventional (non-inverter) generator syncing cleanly with a Quattro 48/8000?
Running a fairly similar setup to what's been discussed elsewhere:
- Victron Quattro 48/8000 (single phase, off-grid rather than grid-tied)
- Cerbo GX with Touch 70
- Victron MPPT 450/100 on a 4.8kWp array
- Fogstar 48V LiFePO4 battery bank (roughly 15kWh usable)
The generator in question is a Yamaha EF6600 — conventional brushed alternator type, not an inverter-generator. I know, I know. The Quattro manual strongly implies inverter-generators are preferred for AC coupling and generator assist, but the EF6600 is what I've got sitting in the shed and it cost a fortune so I'm reluctant to shelve it.
The Quattro's generator input is rejecting it fairly consistently. Frequency wanders between roughly 48.5–51.8Hz under varying loads, which I suspect is confusing the Quattro's acceptance window. I've tightened the UPS function settings in VEConfigure and widened the frequency tolerance slightly, but it's still dropping the connection intermittently.
Questions for anyone who's been here:
- Is there a reliable VEConfigure profile that tolerates conventional generator instability without compromising the inverter's behaviour?
- Has anyone fitted an AVR upgrade to an EF6600 specifically to clean up frequency drift?
- Worth considering a line conditioner between the genny and the Quattro